?     Asked on 1/16/2012by Guest

Will a gas heater operate at the low speed of a dual speed motor?
 Reply

A  Answered on 1/16/2012 by InyoPools Product Specialist Patrick P.

Probably not - Most gas heater will shut off at low GPM levels (20-40) to keep the heater cores from overheating - 20 for 200 BTUs, 40 for 400 BTUs. Depending on your pool system you might get these GPM levels at the low speed but generally these heaters must be run at the motor's high speed.
 Reply


?     Asked on 10/10/2012by Guest

What is the difference between an Electronic and Millivolt ignition?
 Reply

A  Answered on 10/10/2012 by InyoPools Product Specialist Patrick P.

The basic answer is that Millivolt is the old style of ignition, using a standing pilot light. While the electronic ignition uses a spark start system like a gas grill. Electronic ignitions are more efficient in gas usage and also are better suited for high wind areas where a pilot light might get extinguished.
 Reply


?     Asked on 9/8/2015by Paul wood

Do you offer a low nox 366BTU in a CuproNickel?
 Reply

A  Answered on 9/11/2015 by InyoPools Product Specialist Joe S.

RayPak LowNox, Cupro-Nickel Heater 337K BTU NG Elec Ign (2,000'-6,000') MODEL#010132
 Reply


?     Asked on 3/21/2017by Kristen Meester

How do I know if it is cupro-nickel? The only difference I've seen is in the title. The product descriptions are the same between this heater and the #010132
 Reply

A  Answered on 3/21/2017 by InyoPools Product Specialist Andy O.

Hello Kristen- There are two places you would see the differences the first would be in the product name where it lists it as a cupro-nickel and the other would be in the model number which ends in an "x" which is the designation for the cupro-nickel models.
 Reply


?     Asked on 6/28/2017by linda

how far does the pool heater have to be from the house - huntington ny
 Reply

A  Answered on 6/29/2017 by InyoPools Product Specialist Joe S.

For U.S. installations, the point from where the flue products exit the heater must be a minimum of 4 ft below, 4 ft horizontally from, or 1 ft above any door, window or gravity inlet into any building. The top surface of the heater shall be at least 3 ft above any forced air inlet, or intake ducts located within 10 ft horizontally
 Reply


?     Asked on 5/15/2021by Lisa Dayton

Will this meet Riverside County, CA requirements for natural gas pool heaters? This unit would be replacing the 1997 model RP2100 I now have.
 Reply

A  Answered on 5/18/2021 by InyoPools Product Specialist Patrick P.

Yes this Low Nox heater does meet the California standards for pool heaters.
 Reply


?     Asked on 5/15/2021by Lisa Dayton

When referring to gas pipe diameter size required, is it distance from the gas meter to the unit?
 Reply

A  Answered on 5/18/2021 by InyoPools Product Specialist Patrick P.

Yes, that is correct.
 Reply